The purpose of doing the modification is that you are not at the mercy of your pump flowrate. In some case, user would experienced the dreaded stop start function of the chiller. This is due to the pump flowrate not matching what the chiller required. If you have a too fast pump flowrate, it would suck in cold water faster than the chilled water could chill the tank water ( depending on your placement of outlet and inlet tube ). Or if it's too slow, the sensor in the chiller tank would register that the water has already been chilled to the required temperature and prematurely stop its operation.
With the external temperature probe modification, you are not at the mercy of purchasing or using your current pump. BUT there is a minimum flowrate required and that is it should not go below 500lt per hour as it might create a dead zone area in your tank.
The dreaded stop start occur when the chiller internal probe registered that it has chilled the water to the setting the user has programmed but actually it was an error reading. My deduction on the reason why this happen is either the pump flowrate is too fast or the water is not moved quick enough that the chiller internal reservoir probe registered the cooler water from its own internal tank instead of from the incoming water.
The gremlin is in the water reservoir of the chiller.