Can call Derrick, Pacific Cool: 9025 5562 / 9797 9910
Btw don't think the coolant gas will just leak after left un-operate for 4mths. I have been running one for 4 years on and off without topping gas.
Hi there.
I have this Resun CL650 which is not able to lower the water temperature in my 3" tacnk.
I just have a newly filled up tank with the canister filter connected to this chiller.
The chiller was run overnight and did not reached the target temperature (27deg).
After going through, I'm suspecting to be the coolant gas leakage after left un-operate for 4mths.
I also noticed that the coolant gas bowl also slightly hot.
Can you guys help recommend to me where I can get the Resun CL650 coolant gas refilled?
Any idea what is the price range am I looking at?
Thanks......
=D>=D>
Last edited by bossteck; 12th May 2009 at 21:38. Reason: Change to more readable font / color
Can call Derrick, Pacific Cool: 9025 5562 / 9797 9910
Btw don't think the coolant gas will just leak after left un-operate for 4mths. I have been running one for 4 years on and off without topping gas.
Price are more or less estimate below
Transport - $30
Top Up Gas - $40 1 HP n more is $50
Gas Valve - $10
Fan Blade - $40
Chemical Wash - $40
Vacum of connection and compressor - $50 to $150
Replacement Of Chiller Fan - $50 to $180
External Controller - $200
Another for your comparision for price
Chill Down 97993955
Hi there.
Thanks for the contacts given.
I have checked with Chill Power and after on the phone conversation, problem has been narrowed down and also solved.
This is claim to be manufacture defects because the nut connecting the compressor with the heat sink was not done properly leads to coolant gas leakage.
The issued solve by refilling the coolant gas.
Thanks guys.
Last edited by bossteck; 12th May 2009 at 21:39. Reason: Change to more readable font / color